Nate,
RTDs allow temperature measurement by reading the resistance of a sensor. This is normally done by exciting the sensor with a known current and measuring the resulting voltage. There are three general types of RTDs; two-wire, three-wire, and four-wire. Two wire RTDs are less accurate because the wire resistance is indistinguishable from the sensor resistance. Three wire RTDs use two wires on one leg (one to carry the known current and one to measure the voltage) allowing one portion of the wire resistance to be nullified. 4 Wire RTDs use two wires on each leg (one for the excitation current) to nullify the wire resistance. As a result, 4 Wire RTDs are the best ones to use for high precision or long distance measurements. To measure 4 Wire RTDs with FieldPoint, you will need to use the [c]FP-RTD-124 module instead of the [c]FP-RTD-122. With that said, I do not know how well 4 wire RTDs will do at 150 feet. 4-20 mA transmitters will easily handle 150 feet so they will probably be your best option. To measure the 4-20 mA signal, you can use the [c]FP-AI-100, [c]FP-AI-110, [c]FP-AI-111, [c]FP-AIO-600, or [c]FP-AIO-610 modules.
Regards,
Aaron
LabVIEW Champion, CLA, CPI