SysApp,
Since the only modules showing up when you do a Find Devices are the FP-2010 and the FP-DI-301@1, you probably have a bad connection. Remove power to the system and make sure that the terminal bases are aligned properly and that there are no bent pins between the terminal bases, paying particular attention to the pins between the first and the second terminal bases. Also, make sure that you are using the bus cover (ships with the network module) to cover the exposed bus pins on the last terminal base.
The Invalid IAK File error may be caused by providing an invalid path to the IAK file, not providing a path to the IAK file input and not having saved an IAK in FP Explorer, not providing a path and having deleted the last IAK file that FP Explorer used
, or several other similar scenarios. Since you did not provide the error code I can not tell exactly which reason is most likely.
Regards,
Aaron
LabVIEW Champion, CLA, CPI