Hi,
The AIO 610 can only accept current inputs in a +/- 20 mA range. So if your pyrometer is supplying more than 20 mA, then you will receive that out of range error. I would double check what range of current this pyrometer is outputting and then you will be able to see if it's within the specification for the FieldPoint module. If the current is over 20mA, then you have the option of putting in external circuitry, such as a current divider to make the current within specifications. It would probably be a good idea to check with the manufacturer of the pyrometer as well.
Regards,
Hal L.