FieldPoint Family
Under what circumstances would an FP-AI-112 turn itself off?
An FP-AI-112 appears to have turned itself off.  After power was recycled the module is working fine.  Are there any heat sensors or others that would turn a FP-AI-122 off.  All other modules in the bank remained on.
(7,194 Views)
Pete,
There are no heat sensors in any of our modules or controllers that will trip them to turn off.  Most likely, you may just have an aging module.  Be sure to keep an eye on your operation in case you need to cycle the power again.  If this is a critical module and you need to minimize downtime, this may be a sign to order another module now.  If downtime is not a big issue, then hold on until this starts happening more regularly, and when it becomes a problem, you can send the module in for repair.
You may see this happen again within the week, or you may not see this happen for another year.  Please keep that in mind as you consider the need for replacements or repairs.
ColeR
Field Engineer
(7,178 Views)
Cole,
    Thanks........ this module is used in a critical function, has been in service about 2 years  I did note on terminal board (FP-TB-1)  the FP-AI-112 plugs into a component marked RT1.  What function does that component serve?
(7,170 Views)
Pete,
What device is this RT1 connected to?
ColeR
Field Engineer
(7,164 Views)
Hi Cole,
     The FP-TB-1 has a printed circuit board inside.  Looking at the printed circuit board orientated with screw terminals on the bottom, the RT1 component is mounted on the PCB just to the right of the screw terminals.
Pete
(7,130 Views)
Pete,
I'm sorry I read your previous post wrong the first time.  RT1 is a thermistor and is used when CJC is needed for measurements.
ColeR
Field Engineer
(7,125 Views)
Thanks Cole, I greatly appreciate the assistance.
Sincerely,
Pete
(7,120 Views)