FieldPoint Family
Using external power supply with field point modules
hi,
I m using 3 AI111, 3 DO401 and 2 DI301 modules with FP1601 ethernet module. If I m using external power supply, shall I use seperate power supplies for each module or a single one for all. What will be the rating of that Power supply? Kindly answer in detail.
Regards
GNS
(3,440 Views)
There are multiple factors to consider in desiging your system.
1) The FP-1601 requires an external power supply to power itself and the control circuitry of all the IO modules. This supply must be between 11-30 VDC and must be greater than 4.5W + 1.1(Sum of IO module power ratings).
2) The FP-DO-401's require an external power supply between 5 and 30 VDC. This supply is used to power the output channels. The power supply must have a sufficient power rating to power each of the outputs based upon the load each one will draw. Each channel outputs a voltage equivalent to the input power supply. If you need different output voltage levels, use a different power supply for each FP-DO-401.
3) The FP-AI-111 and FP-DI-301 modules do not require external power. Ex
ternal power may be routed through their V&C terminals to take advantage of the terminals and provide loop power to sensors but it is not needed.
4) It is possible to use a single power supply to power the FP-1601 and the I/O modules, however, by doing so you bypass the module to module isolation. To maintain the maximum amount of isolation, you should use one power supply per IO module that requires external power. For a small amount of isolation (I/O to control), use one power supply for the control module and one power supply for the I/O modules.
5) For modules that need to remain isolated, do not connect the V or Vsup and C or Com terminals from one I/O module to the next.
There should be several other Developer Exchange posts that also deal with this issue.
Aaron
LabVIEW Champion, CLA, CPI
(3,440 Views)