lication with OPC server. Can we assure that the time of reading of values for all the channels is the same?. We need to compare those 4 external counting values between them, using the 32 Khz internal clock like a time base reference. Can anybody help us?The answer to your question depends upon several conditions. First, what network module is being used?
If an FP-1000 is being used, with the limitations of the OPC server not supporting items that have multiple analog (count) channels, we can not guarentee the synchronicity of the data. Using the Optomux Commands from the FP-1000/1001 Programmers Reference Manual, http://www.ni.com/pdf/manuals/321632c.pdf , you can use the !F or !G command to read the multiple channels at the same time to achieve the accuracy listed below.
If an FP-1600/2000/2010 is being used, they will normally do a scan of a all channels on a module at a time, then proceed to the next module. As long at the network module is attempting to read multiple channels in a single shot, the data f
rom the FP-CTR-500 will be a relatively synchronized reading (worst case between all channels should be approximately 18 microseconds).
Regards,
Aaron
LabVIEW Champion, CLA, CPI