02-20-2008 02:35 PM
02-20-2008 05:21 PM
You say only pins 2 and 3 are essential, but pin 5 the ground pin is essential as well in RS-232 communications because the transmit and receive pins are referenced relative to the ground pin.
dougl wrote:
I've stripped the cable down to its bare essentials (pins 2 and 3 only) thinking that perhaps there is a noise issue. No help.
Any suggestions are welcome. I've run out of ideas...
Doug Latornell
MDS Nordion, Vancouver
02-25-2008 04:34 PM
Thanks for the reality check, Ravens Fan. Pin 5 was the missing link. The instrument documentation said pin 7 was ground, but I've come to the conclusion that is probably an error held over from when they used to use a 25 pin serial port.
@Ravens Fan wrote:
You say only pins 2 and 3 are essential, but pin 5 the ground pin is essential as well in RS-232 communications because the transmit and receive pins are referenced relative to the ground pin.
@dougl wrote:
I've stripped the cable down to its bare essentials (pins 2 and 3 only) thinking that perhaps there is a noise issue. No help.
Any suggestions are welcome. I've run out of ideas...
Doug Latornell
MDS Nordion, Vancouver