What network module are you using? If you have an ethernet network module (FP-1600, FP-2000, or FP-2010) and have configured deadbands on the channels, you may not be receiving updates because the channels are not changing outside of the deadband range. For example, if you have a channel configured for Celsius readings and a 10% deadband, the smallest detectable change is 0.10 * (270 +1770) = 204 degrees Centigrate. Even a 1% deadband still requires a change of 20.4 degrees to register and update your program.
To find out what deadband is configured with FieldPoint Explorer, right click on the FP-TC-120 and choose Edit This Device. Then choose Channel Configuration, the Percent Deadband setting is in the middle right side of the window.
Regards,
Aaron
LabVIEW Champion, CLA, CPI