FieldPoint Family
Showing results forĀ
Search instead forĀ
Did you mean:Ā
use of Compact FieldPoint controller without backplane
Is the use of Compact FieldPoint controller (say CFP 2110) without a backplane possible and recommended by NI?
Robert
Message 1 of 9
(7,134 Views)
Hi Robert,
   from 9 months I'm using 2 cFP-2020, not connected to a backplane, talking each other via RS232, with a custom protocol, running embedded application.
   The 2 controllers also communicate by Optomux protocol and Rs485 with FP-1001 modules.
   This work quite good, and I had the possibility to talk about this solution with  NI people at NI forums (NI Days and so on).
   Of course, in this way you can use cFP controller as an embedded PC, you don't use cFP architecture modularity.
   I hope this can help you! Have a nice day!
graziano
Message 2 of 9
(7,128 Views)
Splendid Graziano,
embeded PC functionality will do just fine ... have you had any feedback from NI folks if such (mis)use conforms with cFP operating instructions, warranty conditions etc.
thx, Robert
Message 3 of 9
(7,122 Views)
It is entirely possible to use the cFP-20XX and cFP-21XX controllers without a backplane. The primary difficulty in doing so is that you have to create some sort of custom mounting solution and way to cover the exposed electronics (where the module normally plugs into the backplane). Damage to this area may (or may not) be considered outside of warranty by NI.
Additionally, since the backplane is grounded and intended for normal operation, using the controller without the backplane may result in the module no longer meeting some of the EMC/EMI specifications. The module may still meet these ratings, but was not tested for this scenario at the time of its original development.
Aaron
LabVIEW Champion, CLA, CPI
Message 4 of 9
(7,119 Views)
I suppose  warranty condition are for module itself, so it shouldn't matter on how it is stored.... but iyt would be interesting to get an NI answer!
graziano
Message 5 of 9
(7,117 Views)
robertmodic and Graziano,
Though others have had success using a controller not connected to a backplane, this is not an NI recommended configuration. As Aaron mentioned, we have not tested controllers in this configuration, therefore we cannot guarantee that they will meet their specifications.
Hope this helps,
Message Edited by Voltage Viper [DE] on 06-30-2006 11:31 AM
Ryan Verret
Product Marketing Engineer
Signal Generators
Message 6 of 9
(7,084 Views)
Thank you for your support.
regards ...
Robert
Message 7 of 9
(7,063 Views)
While I cannot guarentee compliance specifications without doing more research, NI does not discourage customers from using FieldPoint or Conpact FieldPoint controllers without a backplane. We even offer a mounting kit for the controller by itsself.
Please post again if there are any more questions.
Eric A.
Distributed I/O Product Support Engineer
Message 8 of 9
(6,307 Views)
Hi
   and thanks Eric, we will consider this for the next project!
graziano
Message 9 of 9
(6,281 Views)
