9216 3-wire RTD 100ohm input setup
I am using Q1 2023 LabView with windows 10 and the NI-cRIO 9039. I am using a 3-2ire 100ohm RTD that is working correctly when using a multimeter to measure resistance. I have it connected to an NI-9216 with spring terminal pinout with all equal wire lengths. I have the + of the RTD connected to the RTD + on the 9216 the - connected to the RTD minus and the GND connected to the 9216 COM input. My value in labview is reading -490. When I heat up the RTD is goes further negative. I feel like i could just make a generic variable to multiply by -1 and subtract about 22 to room temperature but I will be off by a couple degrees. How do I get labview to read an RTD correctly? The tutorials I am finding are not helping. I found the one that walks through the steps with the 9217 but I can not switch my device to 3-wire. That does not show up in my labview project or NI MAX. I am at a loss. Could someone point me in the right direction? Where would I find the proper tutorial to read an RTD
(1,049 Views)
The documentation on the NI-9216 seems a bit "scant", but it does say it works in both 3-wire and 4-wire configuration.  This is from the NI-9217 "Getting Started" manual:
2024-05-12_09-37-30.pngHope this is helpful.
(984 Views)
Your system may be configured for a 500-ohm RTD as these can use several different varieties of RTDs.  Ensure that the system is set for a 100-ohm RTD and is wired according to the information provided by Bob_Schor above.
The key takeaway here is the information after the schematic and before the note.
The 3-wire RTD works based upon the voltage reading at the RTD- point.  Based on all wiring being equal in length and resistance, the voltage rise recorded at the RTD- input would equate to two lengths of wire [(Ground->RTD) & (RTD->RTD- Input)].  This means that the voltage loss due to the resistance from the RTD+ to RTD- should equal that from RTD+ to GND or RTD- to GND.  That will leave you the voltage across the RTD.  Now all that is left is to find the resistance of the RTD and convert it to temperature.
Help the Community (and future reviewers) by marking posts as follows:
If it helped - KUDOS
If it answers the issue - SOLUTION
(969 Views)
OK, it turned out my RTD labels didn't line up. The GND went to the +, the - went to GND, and the + went to -. Took me too long to figure that out.
(893 Views)
