06-06-2011 08:39 PM
I am using Vegaflex level transmiiter 61, its range is 0.15 to 32m and I am using DAQ 6251 with voltage ouput as 1 to 5V
I calculated the linear equation as y=7.96x + 7.8125
When I check the volatage while carrying out the measurement the voltage is 2V in multimeter and same in the VI I made.
But when I calculate the level of tank it is 0.689..m in the VI as per the above logic but in the sensor , the value is 0.9m.
Also the tank I am using its maximum level limit is 1.5m only.
What can be the reason for the different result?
06-06-2011 10:01 PM
The linear equation should be y=7.9625x - 7.8125. Minus, not plus.
06-06-2011 11:26 PM
sorry thats mt typing mistake in the forum.
But I am just thinking.
Is the sensor linear or not?
Please see the manual attached I am using Vegaflex 61 cable type
http://www.vega.com/downloads/PI/EN/29657-EN.PDF
Please suggest ..also the tank max limit is 150m
06-07-2011 08:19 AM - edited 06-07-2011 08:24 AM
Some Questions:
The sensor has an current output 4-20mA. To get a Voltage signal at your DAQ you probably use a resistor ... What value(, TC?, actual value?) ?
The sensor needs to be configured. How is the setup for the output? If the lower End is off 0.6% you have your offset.
06-07-2011 08:31 AM
Your reported error is 0.6% .. could be the current to voltage converting resistor, a bad sensor setup... too bad my crystal ball is in recalibration ![]()