09-09-2014 05:14 PM
I have an application that I am using a NI 9208 current input card. The signals that are connected are both looped and single input. The looped powered sensor is connected to AI0, COMM and Vsup. I have a 24 Vdc power supply connected to Vsup and COMM. The other sensors are not 4 to 20 mA looped powered and they are connected to COMM and AI1...AI4. All the sensors share the same 24 Vdc power source.
Can the NI 9208 except both types of connections?
09-10-2014 12:47 PM
Hi ChadAnd,
The 9208 can accept loop-powered and three-wire current transducers. Refer to pages 9-11 of the 9208 Specifications Manual for more information. As far as your AI1-AI4 sensors, as long as they fall within the input range (typical 22mA), you should be fine.