Cascading TF ??

Hello,

 

I used to work with Matlab and I'm in the process of evaluating Labview (specially the Process Control Suite).

This question might appears obvious for some of you since I consider myself as a beginner with Labview.

 

As a test, with the Toolbox CD&S, I've setup a simple control loop (inspired by some examples available in the distribution) for a 1st order process (Gp = 1/(s+1)) implementing the same simple PI controller different ways just to see if things work the same way as in Matlab.

 

I already figured that when I'm using PID object from PID toolbox (graph 1), I have to specify dt = step size. However, I don't understand why Graph4 example where I cascade Gc & Gp, I obtain a flat (=0) response ???

 

I'm using Labview 2010 (evaluation version from NI.com website) and the following toolkits: 2010CDSIM, LV2010SYSIDTK, 2010SIT, 2010PIDFuzzy, 2010MSRT-Win

 

Anyway to cascade TF as in graph4 example ?

 

 

 

 

0 Kudos
Message 1 of 5
(2,978 Views)

Would be a good idea to re-save and post your vi in an earlier version, possibly version 8. Not everyone has the latest version, including myself, so cannot open what you have done,

 

Regards,

 

Lucither

------------------------------------------------------------------------------------------------------
"Everything should be made as simple as possible but no simpler"
0 Kudos
Message 2 of 5
(2,957 Views)

As suggested, I just tried to save to LV v8.5. However, when I tried to load the VI (v8.5), the graph4 example works just fine.

 

So it seems it's related to the fact I'm using version 2010...

I'm surprised since linking TF in serial for a SISO system should be simple.

 

Anybody from NI can explain why I have this issue with version 2010 ? 

0 Kudos
Message 3 of 5
(2,925 Views)

Hello,

 

Unfortunately you are runnning into a known issue with the LabVIEW Control Design and Simulation Module in the 2010 version. Please install the patch:

 

http://digital.ni.com/public.nsf/allkb/F1435BA36246B84186257773007DD70F

 

and you should be able to see something different than a "flat zero".

 

Let me know if that helps!

Barp - Control, Simulation, RTT and HIL - National Instruments
Message 4 of 5
(2,908 Views)

Yes, everything seem OK now ! The patch you recommend solve this issue.

 

Thanks a lot for your help !

 

Jean