Current measurement using NI 9219
Hello, I am trying to do low-current measurement using NI-9219.
Basically, the current will be carried by the jet produced by a process called electrospinning (Please, look at figure).
The current will be from micro to nanoampere, so I think I measure the voltage drop across the resistor and then calculate the current using Ohm's law.
My concern is the setup design (Figure). If I follow this diagram, I am worried that the conductive collector causes serious measurement flaws as itself is a huge resistor since the current is very low (micro-nano).
I am new to electric stuff, so please be generous.
Thanks.
Message 1 of 9
(5,558 Views)
Hi Danny,
have you considered to use an amplifier?
Message 2 of 9
(5,547 Views)
You can lose your external resistor.  The NI 9219 module is capable of measuring currents directly. The NI 9219 computes current from the voltage that the ADC measures across an internal shunt resistor.  According to the datasheet, the input current range of the module is +/- 25 mA, which gives you resolution down to 3 nanoAmps at best.
Message 3 of 9
(5,545 Views)
When measuring the current directly please consider keep those accuracy, stability and noise numbers in mind…
(Resolution is something different than accuracy.)
Message 4 of 9
(5,538 Views)
How much voltage is applied and expected at the measurement point. You may be exceeding the channel to ground ratings of the 9219.
Perhaps an instrumentation amplifier with isolation may be the preferred route to take.
-AK2DM
Message 5 of 9
(5,530 Views)
Thank you for the reply.
1. Maybe it sounds stupid question, but how input range of 25 mA give me 3 nanoAmps?
2. Then new diagram will be like this?
Message 6 of 9
(5,527 Views)
From other literature, they used this setup in diagram with the resistor of 20 Mega ohms. The measured current was about 0.04 micro Amp. So it gives me about 0.8 V.
Message 7 of 9
(5,523 Views)
Accepted by topic author Danny6802
Resolution = input range / (bit depth - 1) = (0.025 + -0.025) / (2^24 - 1) = 2.98 x 10^-9
No.  Current is never measured on a parallel leg.  Current is measured in a serial circuit.  Your current flows from the supply V+ to the tool, to the collector plate, and then to ground, which is also your supply V- (COM) reference.  Just insert the NI 9219 current + and - terminals in line somewhere, so that all current also flows through the module.
Message 8 of 9
(5,515 Views)
Thanks for your help!
Message 9 of 9
(5,503 Views)
