Error 56 (Timeout) on Modbus RTU read
It's not exactly random, but I don't think there's anything there.
Thanks for the concern though. 🙂
Message 11 of 17
(4,746 Views)
Hi Oksavik,
How are you getting on with this issue? If you are still getting the error, this article has a number of steps you can go through to troubleshoot this error:
Timeout Error 56 When Communicating Between Network Devices Using LabVIEW - National Instruments
Kind Regards
Elmunzir
NI Applications Engineer
Message 12 of 17
(4,727 Views)
Thank you. I must admit I had forgotten to follow up on this post.
I verified that it was not the host computer, by trying a secondary computer.
The communication between host and cRIO is working fine.
To verify that the serial (RS485) port on the cRIO is not malfunctioning I did a loopback test.
https://knowledge.ni.com/KnowledgeArticleDetails?id=kA00Z0000019LyOSAU
The port seemed to work fine, as I was able to write and read with no problem.
This makes me believe that the issue must be the daisy-chain of instruments.
I will troubleshoot this by
  • Disconnecting all of them
  • Connect only the first one
  • Test
    • If it works, connect the next
    • Continue until it doesn't work
  • Try to understand what is not working
The article you linked was informative, but mainly with regards to TCP/IP communication. Thank you!
Message 13 of 17
(4,722 Views)
Hey Oksavik, did you find the cause for your problem?
Ingo – LabVIEW 2013, 2014, 2015, 2016, 2017, 2018, NXG 2.0, 2.1, 3.0
CLADMSD
Message 14 of 17
(4,697 Views)
Accepted by Oksavik
We were able to fix the problem, though what caused it remains a bit of a mystery.
When we started looking at how the instruments were connected, we quickly saw that they were in fact not daisy-chained, but connected in a star configuration.
This was much easier to do at the time, and since we have relatively short leads it was not seen as a problem.
When we started disconnecting instruments from the star we found that a single pump was the cause of the issue.
When it was connected, nothing worked; when we disconnected it, everything worked fine.
Turned out that the pump was in a "bad state" of some sort, and after cycling its power it was fine.
How come this pump in a "bad state" messed up the communication for all the other instruments, I don't know. Maybe someone here is able to explain.
Lesson learned:
Try turning it off, and on again.
In this case, not just the computer stuff, but the main circuit breaker as well.
Message 15 of 17
(4,695 Views)
I'm not sure if accepting my own post as "solution" is the right thing to do, but it sort of closed the case for my part.
I would mention that in regards to the error message received when trying to open the Visa Test panel, I read somewhere that this was the expected behavior for a cRIO.
I haven't been able to verify this, but if you're getting this error message when trying to open the test panel on a cRIO, it might not be a symptom of any problems with the HW.
Message 16 of 17
(4,689 Views)
Yes, that's absolutely the right thing as you described the solution in it!
I am a bit baffled that I did not ask about your instruments' connections earlier: Generally, Modbus RTU RS485 is not meant to support star topology wiring. If it works - good. Unfortunately in your case, it produced a tricky problem. Good to hear you solved it!
CLADMSD
Message 17 of 17
(4,680 Views)