Nicola,
First to disable the embedded application from starting, reboot the module with the Disable VI dipswitch (position 6) in the active position. Following the boot-up, the module will not launch your embedded program. Second, reboot the module a second time, this time with dipswitch 6 deactived and the reset dipswitch (position
😎 activated. This will clear the module's IP address and ethernet configuration.
You can then re-install the firmware through FieldPoint Explorer. This will take it as close to out of the box as possible.