Modbus Temperature Device (Slave) Display Value different from Labview displayed Value

I have a LabVIEW code that runs as Modbus master and a Temperature Slave device with a display on it. The problem I have is that the temperature device display is usually greater than what the shown Labview value by 1. There is no mathematical calculation involved in the code except to read a 16 bit holding register address and whose value is just connected to a LAbview indicator. Any help please?

0 Kudos
Message 1 of 26
(4,443 Views)

what does "usually greater" mean?
Give a list of values (display, modbus). Rounding errors are also possible.

Labview 4.0, 5.0, 6.1, 8.6, 2009, 2011, 2012, 2014
If you do not know something, ask me.
0 Kudos
Message 2 of 26
(4,440 Views)

I mean that the value on the device display screen is more by 1 than the Labview modbus value. Im using labview 2017. Examples are: 819 (Device Display) Vs  818 (Labview),  767 (Device Display) Vs  766 (Labview), 809 (Device Display) Vs  808 (Labview) 

0 Kudos
Message 3 of 26
(4,432 Views)

What is the device?  Do you have a link to the manual? Are those Kelvins, Deg C or Deg F?

 

Id guess (my magic 8-Ball is pretty good) the device rounds the value and truncates the register- Add 0.5 of whatever unit to the register value and display as integer 


"Should be" isn't "Is" -Jay
0 Kudos
Message 4 of 26
(4,425 Views)

What does your device manual (BTW: which device, which modbus address) say to this?

 

Regards, Jens

Kudos are welcome...
0 Kudos
Message 5 of 26
(4,423 Views)

The device is a Temp controller. Those are Deg F. Link is https://nicontrols.com/media/pdfs/pixsysatr142usermanual.pdf. Im using modbus register address 1000

0 Kudos
Message 6 of 26
(4,421 Views)

You can also read at 3001..3016 🙂 then the data must match exactly. And about the addition of 1 ... Maybe it's just a bug.

Labview 4.0, 5.0, 6.1, 8.6, 2009, 2011, 2012, 2014
If you do not know something, ask me.
0 Kudos
Message 7 of 26
(4,411 Views)

Use reg 1100 instead and set the display to show tenths of a degree per pg 42.

 

You may need to read 1014 as well.


"Should be" isn't "Is" -Jay
0 Kudos
Message 8 of 26
(4,396 Views)

I read Register 1100 and same Issue existed. Dispay (835)  more than labview value (834) by 1. Register 1104 gave me a different value (382)

0 Kudos
Message 9 of 26
(4,382 Views)

Read the manual again

1104 is setpoint 4

1100 is visualized process (as displayed) 1014 is the CJC temp


"Should be" isn't "Is" -Jay