My cRIO9082 cannot be connected, and its status in the NI MAX shows 'inconsistent IP settings'

Solved!
Go to solution

No, I am afraid not. All the PC cannot connect with RIO through network, but can connect directly through the RJ45 cable.

0 Kudos
Message 11 of 15
(904 Views)

And what are the IP address of the RIO when connected to the network? 

0 Kudos
Message 12 of 15
(900 Views)

It's 10.0.180.105, which is read through NI MAX, although the status shown 'inconsitent IP settings' on NI MAX.

0 Kudos
Message 13 of 15
(899 Views)
Solution
Accepted by RongZou

So you have: 

PC = 143.167.235.134

RIO = 10.0.180.105

 

Then they are not on the same subnet. 

If you stick with the PC settings of 143.167.235.134, then your RIO need to have a IP in the range of 143.167.235.1 to 143.167.235.254

 

If you stick with the RIO setting of 10.0.180.105, then your PC IP needs to be in the range of 10.0.180.1 to 10.0.180.254

 

 

0 Kudos
Message 14 of 15
(894 Views)

Now, my PC's address is 143.167.182.188.  I tried to set my RIO's address to be 143.167.182.180. This really works. Thank you!

0 Kudos
Message 15 of 15
(887 Views)