RavensFan

You are right.  I clean the rest of the VI and it reads ok now.

The address is 4096 (not 4097)

Thank you all.. attached the vi that works.

0 Kudos
Message 31 of 46
(2,147 Views)

attahment- second try

0 Kudos
Message 32 of 46
(2,143 Views)

All I am trying to do is try to read the holding register from this chiller unit but I keep getting this error. I try pinging both address and they seem to be working fine. Is there anyone that can help assist me with my issue?

It would be greatly appreciated

0 Kudos
Message 33 of 46
(2,097 Views)

All I am trying to do is try to read the holding register from this chiller unit but I keep getting this error. I try pinging both address and they seem to be working fine. Is there anyone that can help assist me with my issue?

It would be greatly appreciated if anybody has any suggestions.

0 Kudos
Message 34 of 46
(2,082 Views)

I don't see where you are trying to read a holding register.  You have two functions,  one reading coils and the other reading input registers.

Message 35 of 46
(2,063 Views)

Thank you for the response andI circled it in paint. I am just trying to read the analog values regardless of what the numbers look like. I am really just trying to see some result/indication of numbers.

0 Kudos
Message 36 of 46
(2,031 Views)

The coils are digital outputs and the input registers are the analog values

0 Kudos
Message 37 of 46
(2,026 Views)

Your indicator is called Holding Registers, but the data is coming from the polymorphic Modbus VI that you have set to Read Input Registers.   Input registers and Holding registers are different.  The name of the indicator doesn't matter at all.  But if you are trying to access a holding register, but are using the input register function, then you will get an error.

 

Also be sure that the parameters you are feeding into the function are correct.  For instance, the constant 65535 seems rather large. I can't tell from your screenshot what constants go where since many of your wires aren't straight or are running backwards.  Try using the block diagram cleanup tool on the toolbar.

Message 38 of 46
(2,009 Views)

Okay thank you very much. Attached is me changing the read input registers to holding registers so that I may be able to read values from my modbus so I put an array indicator to do so. my 65000 thousand value was just me testing values out so that I may find a solution but the same error occurs when I have  a small value or large vaule there. I just keep getting this error 6002 

Download All
0 Kudos
Message 39 of 46
(1,989 Views)

You have both coils and registers starting at address 0.  That may be possible, but on many devices, it is not.

 

Have you read the communications manual for the device?  Have you tried using any 3rd party modbus monitoring programs to see if they work?

 

Try attaching a link to the manual.  6002 is for an invalid address.  So I'm suspecting you are callling out the addresses properly in your VI.

 

Here is a document that can help you understand the modbus protocol.  http://www.modbus.org/docs/Modbus_Application_Protocol_V1_1b3.pdf