RT FIFO results in 100% cpu load?
I'm trying to replace some queues with RT FIFOs on a cRIO9074 target (using LV2011), which should be rather easy as the API is very similar for both:
This example VI works for sure: the lower loop puts an I32 into the FIFO each 100ms, the upper loop should wait for "timeout" (set to 50ms) before attempting to read a new element from the FIFO. For this example the upper loop should run (about) 2-3 times for each iteration of the lower loop due to 50ms timeout.
The problem I have is: it reports 100% cpu load and I don't get why it says so:
Where does this example VI burn 100% cpu load? Does the RTFIFORead just poll the current FIFO state?
(5,626 Views)
Accepted by topic author GerdW
Have you checked if a timeout of >100ms also creates 100% CPU load?
Please note that the Create FIFO provides configuration of reading and writing for polling vs. blocking. Refer to the help for detailed information.
Norbert
Norbert
Expert: Geometry
(5,614 Views)
Hi Norbert,
thanks for your comment on the blocking/polling behaviour. That's what I missed when replacing queue by RT-FIFO…
Default behaviour is to poll for both read and write access.
Results:
- setting timeout to >100ms still results for 100% cpu load for default polling modes
- setting blocking mode for atleast read access gives <15% cpu load for this example VI…
(5,605 Views)
Hi GerdW, Hi Norbert,
thanks a lot for sharing this problem and its solution. I searched two days for the reason of the high cpu load. And it really was "just" changing the r/w modes to blocking. I wonder, if it wouldn't be better to change the default value to blocking.
Kind regards,
skusie
(5,417 Views)
skusie,
the default setting is polling (with maximum speed, hence the 100% CPU load) is the fasted method to react on a new elelemt. For most RT applications, this is by far more important than 100% CPU load.
I am not sure, so please take care with the following:
The polling should have the priority of the caller, so if the FIFO Read is contained in a low(er) prioritized VI, it should create 100% CPU load, but other threads may preempt the polling.
Norbert
Norbert
Expert: Geometry
(5,403 Views)
