Hi,
I’m having problems using RT Reboot Controller and RT Ping Controllers from the Real-Time Utilities palette with LabVIEW 7.1, but only with PXI-8184 controllers. This work fine with PXI-8175.
The attached VI will list all the 8175 on the subnet, but none of my 8184. However, I can ping and FTP all my 8184. If Local Subnet? is TRUE, I don’t get any error, but the RT controller doesn’t reboot. If it is FALSE, I get: Error 63 occurred at TCP Open Connection in FPC open connection.vi->RT Ping Controllers.vi->MssUT-RebootController.vi. All 8175 and 8184 are on the same subnet and ahve the same IP settings (mask, gateway, DNS server). None of them is locked with a password.
What’s wrong with this VI and 8184 controllers? Please don't tell me to upgrade to LabVIEW 8.2, I can't, these systems are under production in 3 sites in 2 countries. We already have 16 PXI-8175 deployed that control cars from trains in hump yards.
Thanks,
Patrick.
01-30-2007 02:10 PM
03-05-2013 01:34 PM
Hi Partha,
I am also getting the similar problem when i try to restart the PXI 8196 controller programatically. Did you already found any solution for this problem?
03-06-2013 01:43 PM
Balaji,
As stated above, the device was released after LabVIEW 7.1 so it was not showing up in the list of devices. There is a link above to a Knowledgebase article that discusses that and provides a library that will fix the problem.
Regards,
03-06-2013 02:30 PM
Thanks Nunnya, It worked 🙂