Valve controls
I checked the tutorials and modified the VI but the condition is met but the VI fuctions very fast.
The valve switch too fast.
May be still some error
Message 11 of 16
(848 Views)
I changed a bit. Please the modifed one.
Message 12 of 16
(846 Views)
You probably have a race condition with your local variables.  This may be causing part of your timing problem.  The BYPASS VALVE local to the right of the case structure may execute before or after the case structure, probably before. Regardless of which occurs first, the other write to the local will occur within microseconds.  You can use shift registers to help eliminate the locals.
If you want to set that valve false after a short time, you should add a case to reset it and call that case after any case which sets it true.
A 100 ms cycle time is rather fast for most valves.
Lynn
Message 13 of 16
(836 Views)
Thanks now I realized my mistake in the VI.
That means I need to put one more case structure for resetting each valve. I changed the VI, but then the conditions are not met. Please see.
Ya I agree but this is a small part of the big program and oveall program should work in 100ms.
Still the valves do not stay open for long. They just switch on/off all the time. The element value can be from 0 to 5V only.
element element 2 Bypass valve Main air valve Vent valve
0               0               Open             Close              close
1               2                 Open          Close               Close
2                3               Open            Close              Close
3                 3              Close            Open              Close
4                 1               Open               Close           Close
1                 4                Close             Close            Open
etc few conditions are bein overlapped so all valves are open
Actually,
I wish the Bypass is for equalizing the pressure of two Pressure transmitter PT1 and PT2.
When PT1=PT2 the Main air valve open
when PT1 is 4 the only vent should open
Please the logic file also.
Message 14 of 16
(820 Views)
I do not completely understand your logic diagram or the chart in your text.  What happens in the Valve Operation boxes? Do the valves open Close? Change from one state to the other?  If they only open in those boxes, when do they close?
Referring to the chart in your text: What happens when the values of the elements are not integers? Also, it is generally not a good idea to do Equals? comparisons on floating point data because very tiny, physiclaly insigificant, differences can prevent two values which are very close to each other to compare as Not Equal.  Use In Range & Coerce to test a small window above and below the nominal values.
Lynn
Message 15 of 16
(812 Views)
do not completely understand your logic diagram or the chart in your text.  What happens in the Valve Operation boxes? Do the valves open Close? Change from one state to the other?  If they only open in those boxes, when do they close? I think dont consider the flow chart.
Yes think that is better possiblity I think we cannot make the logic based on the comparisons only it needs some range.
I changed the VI but still logic is note yet met.
Message 16 of 16
(807 Views)