I could not find any examples that would do Feedforward or Predictive control without any additional add-ons. Control applications such as this, are currently handled in the add-ons that you have found: System Identification Toolkit, Control Design Toolkit and ideally the SoftMotion Development Module.
01-02-2008 01:25 PM
Charlie,
Look in the PID tool kit.
Ben
01-02-2008 08:59 PM
Look at the example: Simulation - Cascade and Feedforward Surge Tank Level.vi that comes with LabVIEW Real-Time or with the PID Control Toolkit.
Here is the screen shot of it.
01-02-2008 08:59 PM - edited 01-02-2008 09:01 PM
Look at the example: Simulation - Cascade and Feedforward Surge Tank Level.vi that comes with LabVIEW Real-Time or with the PID Control Toolkit.
Here is the picture if you want to see the controller implemented in LabVIEW. The Feedforward is a Lead-Lag block. Hope this helps
01-02-2008 11:04 PM
01-03-2008 12:11 AM
Say it as LV for LabVIEW, not LB that means the Unit for Mass...
Wormwood wrote:
... so does this mean that LB...
01-03-2008 12:16 AM
01-03-2008 12:45 AM
Wormwood wrote:
From what i i've seen from the example, it didnt mention about the deadtime. And is there exactly a block for a 1st order lag?