10-18-2005 08:35 AM
10-18-2005 08:55 AM
Hello James,
are there any errors on the signals you recive?
In the scope from -3V to +3V the signal from the RS-232 is not defined. The value defined signal is logic high in the scope from -3V to -15V and logic low in the scope from +3V to +15V. Are the signals ot in these limits?
Regards ThomasD
10-18-2005 09:26 AM
10-18-2005 10:11 AM
10-18-2005 10:53 AM
I would think that a blocking cap would also reduce the effectiveness of your noise injection. I was assuming that the problem is the apparent output impedance of the AO. If this is the case, you probably just need to use an op-amp to boost the impedance that you present to the serial line.
Although, now that I think about it, I know that RS422/485 are supposed to have termination resistances in the 0-200 ohm range. I can't imagine an AO output loading that significantly. I don't know what the electrical specs for RS232 (other than the voltages, of course) are offhand, though.
10-18-2005 11:18 AM
I agree with everything siad by Trager!
RE:rs-232 spec
That was inveted before standards were invented!
I believe it was high impeadance becuase you could wire more than one recieve line in parallel and get away with it most of the time. It was also limited to 50 feet max cable run.
Ben
10-18-2005 11:55 AM