01-07-2010 03:23 PM
The project was originally configured in LookoutDirect, then converted to Lookout 6.2.
One one computer I have a seperate Runtime and Development packages. This computer has been working satisfactoraly for two months.
Insatlled second runtime software on computer two, but cannot launch project because of class errors.
Can I copy the entire National Instrument folder from one computer to the other to correct this.
thanks
John Peterson
Solved! Go to Solution.
01-07-2010 04:33 PM
You need to copy the appropriate driver over.
DO NOT COPY THE WHOLE FOLDER!
Mike
01-10-2010 07:43 PM
01-13-2010 05:31 PM
01-14-2010 10:02 AM
Problem solved
Believe drivers are DSComm4.cbx and Meter4.cbx, but don't bother moving them. Tried every conceivable location.
You must INSTALL the driver on both computers.
Driver from Automation Direct(PC-DL-PLUS LOOKOUT DIRECT PLUS DRIVER OBJECT SFTWRE)
From the responses I think their is more than one with the problem.
Also make sure the tages are not pointing to the computer name. Tag path should start with "..\" or "..\..\" (test on yours) to work on both computers. Computer name appears depending on how you drill down to the PLC address. This doesn't stop the project, just gets rid of the red X's on the second computer.
Thanks for your responses
John Peterson