Clearing Nusance alarms

We have had several ocasions where a faulty sensor has generated so many alarms
that is swamps the rest of the alarms. Short of editing the lookout files
is there any way to filter out these alarms until the sensor is fixed ? Normaly
the users have to resort to shorting out the alarm signal physicaly when
this happens.
0 Kudos
Message 1 of 3
(3,386 Views)
We eliminated the same kind of sensors problem
by writing a kind of alarm processing
subsystem. Each faulty sensor reading doesn't
trip an alarm immediately, giving it a time
to recover. Also, we can enable/disable alarm
processing by clicking a pushbutton.
This requires some programming,
of course.

Sergei

Andrew Graham wrote:

> We have had several ocasions where a faulty sensor has generated so many alarms
> that is swamps the rest of the alarms. Short of editing the lookout files
> is there any way to filter out these alarms until the sensor is fixed ? Normaly
> the users have to resort to shorting out the alarm signal physicaly when
> this happens.
0 Kudos
Message 2 of 3
(3,386 Views)
I created a panel of switches (displayed as checkboxes) to disable the hi/lo alarm
settings. I could have used a symbolicLink to avoid creating so many switch
objects, but I like the visual panel --- easy to see what is currently disabled.
When a sensor gets into an oscillation around the alarm setting, the operator can
open the Override panel and disable that specific alarm. For example, my alarm
objects have this form:

Name:Alarm_heliumbottle Alarm area:Ops
Message="OUT OF TOLERANCE Helium Bottle Pressure: "&
..\heliumbottle&" psia"
Signal=..\heliumbottle
Lo Level=if(Switch_heliumbottle_lo,0,500)
Lo-Lo Level=200

If the switch is on, then the lo level is set to 0 psia, below the Lo-Lo level of
that sensor. For my app, I don't want the operator's
to override the Hi-Hi and
Lo-Lo alarms, but the same logic could be applied to them.

I also added a Reset Button to my panel and linked it to the panel's $Alarm (to its
connection Ops.ack). That way all the Ops alarms can be silenced with a single
click.

Andrew Graham wrote:

> We have had several ocasions where a faulty sensor has generated so many alarms
> that is swamps the rest of the alarms. Short of editing the lookout files
> is there any way to filter out these alarms until the sensor is fixed ? Normaly
> the users have to resort to shorting out the alarm signal physicaly when
> this happens.
0 Kudos
Message 3 of 3
(3,386 Views)