Lookout
Compiling error
Hi all,
I'm using lookout 5.1.  I'm trying to port the working files to 6.2.  When the .lks file is opened and recompiled I get the following error.
..._scada.lks(29449): error: Variable value expected: '"Timer_sound_Lookout_alarm"'.  I think I work around this some time in the past but all the alarms went silent.  Any thoughts?
(7,051 Views)
The error means a variable value is expected, however the "Timer_sound_Lookout_alarm" is not.
Could you upload your lks file to ftp://ftp.ni.com/incoming? It is not easy to specify how to troubleshoot this error.
Ryan Shi
(7,035 Views)
Hi Ryan,
I uploaded the .lks file to your ftp site as norwell_scada_lks.zip
Jack M
(7,012 Views)
Open the lks file in text editor, go to line 29449. Or you can search for "Timer_sound_Lookout_alarm" and you will find this line
Sound_controls\PlayWave_on_alarm= new PlayWave ("Timer_sound_Lookout_alarm",
Remove the double quotes. The Timer_sound_Lookout_alarm is a pulse object, which should not be in quotes.
Ryan Shi
(7,002 Views)
Accepted by topic author jmcinnisjr
Ryan,
Thank you, that solved the problem.
Jack M
(6,989 Views)
