Davidd,
The nuetralzone object work well for this problem. When the high level is reached, it will give you an alarm. On the reset of the alarm you can set to the alarm value minus a value the bin must drop before it resets the alarm.
If you are wanting a time delay, you can attach a timer object to the high level in the bin and then attach the alarm object to the timer. This will give you a time delay before the alarm becomes active. After the alarm is activated and if the high level switch resets itself, the timer will reset and a new alarm will be generated.
Hope this helps.
DButler
12-21-2005 02:55 PM
We both talking Lookout here? I don't see any way to recieve a signal when an Alarm has been Acknowledged, nor do I see any way to receive a signal when a specific alarm has gone inactive.
If there is a way, please let me know. That is exactly what I'm looking for.
David Dudley