Poll DL06 PLC and display values on WEB page

Can someone tell me how to poll a Automation Direct DL06 PLC?

At a remote location I have:
DL06 PLC
ECOM-100 Ethernet Card
FO-04D1 Analog card

At the office I have Lookout v5.1 and want to use a VSAT, and Ethernet, to get the remote data.
Do I need any additional software to be able to display this data on a web page?
Can i allow customers to access different pages via the internet, with username and password?
It looks like i need to have the DirectLogic software from AutomationDirect. Does this also server as the OPC server?
Can I install the s/w on any p.c. at the office or do i need a server?
Are there any tutorials that i can download?

Thanks for any help....


0 Kudos
Message 1 of 4
(3,810 Views)
yea i'm interested in this also...somebody.....speak.......
0 Kudos
Message 2 of 4
(3,794 Views)
You do need the DirectLogic driver if you use Lookout. It's an OPC server, built into Lookout.
If you want to do web page for client, you need a web server, such as IIS or Apache.  Lookout can generate the client process as html file.
Ryan Shi
National Instruments
0 Kudos
Message 3 of 4
(3,778 Views)
Use the Modbus driver, select Modbus TCP, and enter the IP address setup on the ECOM module.
Mike Crabtree - Lead Developer