06-15-2012 02:41 PM
This is generic , so I won’t go into the hardware unless necessary, range is simplified 0-20Ma in, 0-20 scale out.
I am having problems with scaling in Lookout, my input is 0-20Ma, input conversion is done in BCD for a unipolar FS output of 16533.
My scaling in Lookout is; raw 0-16533 / eng units 0-20
The readings are like this;
Input - output
0Ma. - 0
4Ma. – 2.52
12Ma. – 11.27
20Ma. – 20
So I tried converting to BIN unipolar FS output of 4095
My scaling in Lookout is raw 0-4095 / eng units 0-20
The readings are like this;
Input - output
0Ma. - 0
4Ma. – 1.65
12Ma. – 12
20Ma. – 20
What am I missing?
06-21-2012 02:59 PM
Create a display to show the raw or unscaled units at each of the mA steps. This will probably give a clue. What is your source transmitter? Is it linear or is it some other function.
06-25-2012 12:53 PM
Like Jim posted, what is the RAW unscaled reading at each analog step.
What is generating your test measurements (0,4,12,20mA)?
06-26-2012 09:27 AM
The source is an Altek calibrator that I checked against another meter. The raw values are;
ma. read calculated
0 0 0
5 4135 4133.25
10 8273 8266.5
15 12405 12399.75
20 16533 16533
Looks like a nonlinear a/d converter, but I didn't expect the scaled values to be that far off.
06-27-2012 12:06 PM
Your numbers look quite linear to me, only a few counts off what is expected. The values given scale just fine with my testing. The puzzle is fun but I think it's time for you to share more about your hardware and what driver object you are using. The only hardware I have handy that uses BCD datatypes are automation direct PLCs. Every thing scales just as it should. i.e 2084 BCD =2.52 scaled, 3306 BCD scales to 3.99, likewise 3306 Dec scales to 3.99 and 2084 Dec scales to 2.52.
When you did your test what where the scaled values at each step?
%maReadScaled
000??
2554135??
751512405??
1002016533??
06-27-2012 12:13 PM
Sorry my formating was messed up in the previous response.
% ma read scaled
0 0 0 ??
25 5 4135 ??
75 15 12405 ??