Encoder Triggered acqusition with motion card RTSI buss
I am looking at using the PCI-7334 Motion card to control a motor, we also need to measure a analog signal via an 18-bit NI DAQ card, triggered to the motor encoder. Can I via the RSTI buss do this? (I know the Motion card has analog - but 12-bit is not enough resolution for us.)
Does the standard set of Motion Drives support this? Do I need the wiz-bang motion drivers?
I would like to avoid wiring the encoder to boths cards to avoid noise/loading problems.
Regards
Jack Hamilton
(3,296 Views)
Jack,
The NI Motion Controllers have he ability to generate a signal when the encoder matches a specified position. We call these breakpoints or position compares. These signals can be routed via RTSI or the PXI backplane to the DAQ board.
The PCI-733x/4x board support single shot breakpoints. For every breakpoint you enable it in software. The maximum breakpoint frequency is 150 Hz. The PCI-735x board supports periodic and buffered breakpoints. These are enabled by the hardware and support breakpoint frequencies of 4 Mhz and 2 Khz respectively.
Rodger S.
(3,295 Views)
Hi Jack,
If you are going to be using the NI DAQ card, the method Rodger mentioned should be just what you need. In addition to this method, I would just like to point out that the 7350 series of Motion Controllers has a 16 bit A/D converter. This still might not be enough resolution for your particular application, but it is available if you need it!
Robert
(3,285 Views)