Motors move with P7000 but not with MAX

Zach,

 

Unfortunately I can't use the other line, it is in 24/7 automated operation and I can't stop it during someone else's run.

 

Is there another way to test connections?

0 Kudos
Message 11 of 16
(1,673 Views)

Hello,

 

Have you also verified that the Limit LED, Fault, and Enable switches have been configured identically to the other one that is working for you? Can you check the output of the Enable pin (pin 6) to see if that changes when toggling between kill/halt?

 

-Zach

0 Kudos
Message 12 of 16
(1,654 Views)

Hi Zach,

 

I believe everything is wired the same as on the other (working) set-up, I copied all the wiring from there, but I no longer have access to that set-up and can't double-check. 

 

The limit and home LEDs respond on the UMI, when I hit a switch the light goes off. How do I check the output of the enable pin? And is that the enable pin on the UMI or the P70360?

 

 

0 Kudos
Message 13 of 16
(1,611 Views)

Hi mishka,

 

Zach is referring to Pin 6 on the UMI. If the Enable output is deactivated, the DISABLED LED should light up. You can configure the Enable output to be either active-low(down position) or active-high(up position) using the Enable switch. Can you verify that the Enable switch is functioning correcting?

Andy Chang
National Instruments
0 Kudos
Message 14 of 16
(1,603 Views)

Hi Andy,

The switches are currently set at: FAULT active low, ENABLE active high, LIMIT active high.

If I change enable to active low, the lights stay orange and the disable LED does not come on.

If I change Limit to active low all the lights go out.

If I chage fault to active high the disable and fault LEDs come on.

0 Kudos
Message 15 of 16
(1,599 Views)

Hi mishka,

 

Here's at least some expectations:  the motor should not moved when the disabled light is on.  The disabled light should come on when a fault occurs.   

 

Also you may want to take a look at this DeveloperZone.  The article is for the 7764, but the concepts for limits, faults, enable/disable should be the same.  

 

Here are a couple other related documents as well:

http://digital.ni.com/public.nsf/allkb/CD29A0A9D420D46386256C47005DABA6?OpenDocument  

http://digital.ni.com/public.nsf/websearch/0B2217C7F1293E17862569E70001267E?OpenDocument 

 

 

I hope this helps!

 

 

Kristen H.

0 Kudos
Message 16 of 16