Position Control of compumotor linear servo table and GV-U6E with PCI-7344
I'm referring PCI-7344 (not 7334).
I have the GV-U6E which is a drive only and does not possess control functionality. the drive only version does not store or use programs. So, serial commands can not be sent through COM port by LabVIEW even though A few basic commands can be emulated.
I am trying to do position control as I mentioned. For example, the motor should move A point to B point exactly with a certain speed. The points must be aboulte position.
I would like you to see the reference comment that I have been contacting with in your website forum.
http://exchange.ni.com/servlet/ProcessRequest?RHIVEID=101&RPAGEID=135&HOID=506500000008000000DD490000&USEARCHCONTEXT_CATEGORY_0=_14_&USEARCHCONTEXT_CATEGORY_S=0&UCATEGORY_0=_14_&UCATEGORY_S=0
Regard,
Jin Ho Lee
----- Original Message -----
To:
Sent: Thursday, September 26, 2002 5:00 PM
Subject: Re: (Reference#1549-QYW196) "Position Control of linear servo table and GV-U6E with PCI-7344
> Note: Your reference number is included in the Subject field of this
> message. It is very important that you do not remove or modify this
> reference number, or your message may be returned to you.
> JinHo. Compumotor is a very popular brand, and I know of several customers
> who integrate our 7334 with Computmotor drives. However, when you say that
> the MAX configuration doesn't fit in the compumotor drive settings, are you
> referring to the specs from the 7344? It looks like the 7344 and the
> Compumotor will work well together through a UMI break out box. If you're
> referring to specific commands that the Compumotor receives, I'd have to
> know more about the protocol. If the Compumotor needs serial commands,
> then you can send them through the computer's COM port from LabVIEW.
> Please let me know exactly what kind of configurations you're trying to
> set. The 7344 can be completely configured in MAX and LabVIEW.
> Best Regards
> Kyle Voosen
> Applications Engineer
> National Instruments
> http://www.ni.com/support
> Problem Description :
> "Position Control of compumotor 406LXR linear servo table and GV-U6E(motor
> drive) with PCI-7344"
> "Since I had the answers referring:
> http://exchange.ni.com/servlet/ ProcessRequest?RHIVEID=101&RPAGEID=135&
> HOID=506500000008000000DD490000& USEARCHCONTEXT_CATEGORY_0=_14_&
> USEARCHCONTEXT_CATEGORY_S=0& UCATEGORY_0=_14_&UCATEGORY_S=0
> Wiring step was done well. However, I still have a problem that MAX
> configuration doesn't fit in compumotor drive settings. Therefore, the
> setup is shown below, and I want to know how I can set up PCI-7344
> configuration in MAX or LabVIEW VI.
> Uploaded from device address 0
> Gemini GV Servo Drive Setup
> Motor Setup
> DMTR 1703
> Motor ID (406-x-LXR-M-x-D13-x-x-x-x-E5-x-x-x)
> DMTIC 2.48
> Continuous Current (Amps-RMS)
> DMTICD 0.00
> Continuous Current Derating (% derating at rated speed)
> DMTKE 17.6
> Motor Ke (Volts (0-to-peak)/krpm)
> DMTRES 10.10
> Motor Winding Resistance (Ohm)
> DMTJ 119.300
> Motor Rotor Inertia (kg*m*m*10e-6)
> DPOLE 1
> Number of Motor Pole Pairs
> DMTW 40.5
> Motor Rated Speed (rev/sec)
> DMTIP 7.40
> Peak Current (Amps-RMS)
> DMTLMN 3.4
> Minimum Motor Inductance (mH)
> DMTLMX 3.4
> Maximum Motor Inductance (mH)
> DMTD 0.000000
> Motor Damping (Nm/rad/sec)
> DMTRWC 0.23
> Motor Thermal Resistance (degrees Celsius/Watt)
> DMTTCM 20.0
> Motor Thermal Time Constant (minutes)
> DMTTCW 0.33
> Motor Winding Time Constant (minutes)
> DMTAMB 40.00
> Motor Ambient Temperature (degrees Celsius)
> DMTMAX 90.00
> Maximum Motor Winding Temperature (degrees Celsius)
> DHALL 1
> Disable Hall Sensor Checking
> DMTLQS 0
> Set Q Axis Inductance Saturation
> DMTLDS 0
> Set D Axis Inductance Saturation
> DTHERM 0
> Disable motor thermal switch input
> Drive Setup
> DMODE 2
> Drive Control Mode
> DRES 8400
> Drive Resolution (counts/rev)
> DPWM 16
> Drive PWM Frequency (kHz)
> SFB 1
> Encoder Feedback
> ERES 8400
> Encoder Resolution (counts/rev)
> ORES 8400
> Encoder Output Resolution (counts/rev)
> DMEPIT 42.00
> Electrical Pitch (mm)
> SHALL 0
> Invert Hall Sensors
> DMTLIM 1.5
> Torque Limit (Nm)
> DMTSCL 1.5
> Torque Scaling (Nm)
> DMVLIM 119.000000
> Velocity Limit (rev/sec)
> DMVSCL 119.000000
> Velocity Scaling (rev/sec)
> Load Setup
> LJRAT 0.0
> Load-to-Rotor Inertia Ratio
> LDAMP 0.0000
> Load Damping (Nm/rad/sec)
> Fault Setup
> FLTSTP 1
> Fault on Startup Indexer Pulses Enable
> FLTDSB 1
> Fault on Drive Disable Enable
> SMPER 8400
> Maximum Allowable Position Error (counts)
> SMVER 0.000000
> Maximum Allowable Velocity Error (rev/sec)
> DIFOLD 0
> Current Foldback Enable
> Digital Input Setup
> INLVL 11000000
> Input Active Level
> INDEB 50
> Input Debounce Time (milliseconds)
> INUFD 0
> Input User Fault Delay Time (milliseconds)
> LH 0
> Hardware EOT Limits Enable
> Digital Output Setup
> OUTBD 0
> Output Brake Delay Time (milliseconds)
> OUTLVL 0100000
> Output Active Level
> Analog Monitor Setup
> DMONAV 0
> Analog Monitor A Variable
> DMONAS 100
> Analog Monitor A Scaling (% of full scale output)
> DMONBV 0
> Analog Monitor B Variable
> DMONBS 100
> Analog Monitor B Scaling (% of full scale ouput)
> Servo Tuning
> DIBW 1500
> Current Loop Bandwidth (Hz)
> DVBW 100
> Velocity Loop Bandwidth (Hz)
> DPBW 40.00
> Position Loop Bandwidth (Hz)
> SGPSIG 1.000
> Velocity/Position Bandwidth Ratio
> SGIRAT 1.000
> Current Damping Ratio
> SGVRAT 1.000
> Velocity Damping Ratio
> SGPRAT 1.000
> Position Damping Ratio
> DNOTAF 0
> Notch Filter A Frequency (Hz)
> DNOTAQ 1.0
> Notch Filter A Quality Factor
> DNOTAD 0.0000
> Notch Filter A Depth
> DNOTBF 0
> Notch Filter B Frequency (Hz)
> DNOTBQ 1.0
> Notch Filter B Quality Factor
> DNOTBD 0.0000
> Notch Filter B Depth
> DNOTLG 0
> Notch Lag Filter Break Frequency (Hz)
> DNOTLD 0
> Notch Lead Filter Break Frequency (Hz)
> SGINTE 1
> Integrator Option
> SGVF 0
> Velocity Feedforward Gain (%)
> SGAF 0
> Acceleration Feedforward Gain (%)
> Regards,
> JinHo"
> NI Software :
> LabVIEW version 6.0
> NI Hardware :
> Motion Control device PCI-7344
> Driver Version :
> no
> OS :
> Windows 2000
> CPU :
> Pentium
> RAM :
> 128
> Vendor :
> DELL
> Customer Information :
> Jin Ho Lee
> North Carolina State Univ.
> US
> livecalm@chollian.net
> Ph: (
> 919
> 512-9929
(4,690 Views)
We have successfully done several projects using the Parker-Compumotor Gemini GV servo drive and the NI-7344 and the NI UMI-7764 breakout box.
The secret is getting the correct Parker-Compumotor Gemini cable that plugs into the GV's 50 pin drive I/O connector on one end and has "flying leads" on the other end which you connect to the NI UMI-7764.
Then set up all of the motion parameters that are unique to your application in MAX. Then tune the motion gains in MAX.
We have also written an ActiveX interface to the Gemini's RS232 port to download GV programs or set GV parameters from LabVIEW.
(4,690 Views)
Thanks, but I have already wired Gemini cable (GV's 50pin drive I/O connector) on UMI-7764, as the statement was mentioned. However, the motion parameter doen't fit to my application in MAX. That's why put the parameters of servo drive configuratio above.
I am curious of the ActiveX interface. Could you let me know how it works in detail.
Jin HO Lee
(4,690 Views)
I also need to contact you directly if possible.
Email me
livecalm@hotmail.com
Thanks.
(4,690 Views)
Yes, we used an NI PXI-7344 motion control card with an NI UMI-7764 box connected to a Gemini GV-U12E servo drive. (which is a drive only.)
We did positional control in absolute position mode.
I can send you an AutoCAD schematic detailing how to connect the UMI-7764 to the Gemini GV servo drive.
In regard to the Rs232 interface to the GV servo drive,
the GV drive only model is "configurable" not "programmable". You can create unique GV configuration files with Compumotor's Motion planner then download the configuration via Rs232 using LabVIEW as desired. Or, using LabVIEW via Rs232 you can change individual GV drive parameters on demand,
or use the GV's two analog outputs back to LabVIEW's analog inputs to measure commanded motor current or torque, etc.etc.etc
(4,690 Views)
I will appreciate it if you attach the file on this forum, or email to:
(4,690 Views)