03-24-2009 04:23 PM
We are using the MID-7604 Power Drive to the motor system.
03-25-2009 12:44 PM
Can you attach a sketch of how you wired the motor to the drive.
Have you referred to the manual, have you set the DIP switches for peak current accordingly (pgs 13-15)?
Have you tried setting DIP switch 5 off to disable current reduction?
http://www.ni.com/pdf/manuals/372454e.pdf
-AK2DM
03-25-2009 04:55 PM
Yes, the DIP switches have been set to current reduction mode. How does that impact holding torque?
Anyways, there seems to be some holding torque now! It seems enough for our purposes at the moment. I'm not sure what changed recently to cause it to work now, but no complaints.
03-25-2009 05:04 PM
The manual states:
You can configure the MID-7604/7602 stepper drivers in a current
reduction mode on a per-axis basis. This configuration is useful to
minimize motor heating when you are not stepping. With current reduction
enabled, the current decreases by 50% when no stepping has occurred forapproximately 500 ms. DIP switch 5 controls current reduction on a
per-axis basis. When this DIP switch is on, current reduction is enabled.
When this DIP switch is off, current reduction is disabled. The factory
default setting is current reduction enabled.
03-26-2009 10:54 AM
Cosmund,
Having current reduction mode enabled on the drive will reduce the holding torque. This is because the current drawn by the motor is what causes it to stay at its present position. (This is how you can tell if a stepper motor is properly powered; it is be a lot easier to turn when it is not powered.) So, if the amount of holding torque that you are seeing right now is not enough, you should change the dip switch setting to disable current reduction.
-Christina
03-26-2009 01:49 PM
Christina,
Thanks for specifying the relationship between current reduction and holding torque. It was not very clear from the manual.
cosmund