I always get 0mA with the following: I'm using a 9203 to measure pressure from an Omaga PX-309. The transducer has two wires, red and black. Per Figure 3 in the NI 9203, I've connected the red lead to an AI channel on the 9203. The black lead is connected to a power supply (+) side at 30VDC. The negative side of the power supply is connected to the COM terminal on the 9203.
Two other channels work fine. They come directly from a 9265 analog out.
In DAQmx the two channels (from 9265) are opened with a Create Channel, and the single channel (from PX-309) is opened with its own Create Channel.
Any ideas about my problem here??
Solved! Go to Solution.
07-30-2009 02:34 PM
Greg:
According to the Omega literature:
http://www.omega.com/Pressure/pdf/PX309.pdf
The red lead is (+), the black lead is (-). Good thing the unit has reverse polarity protection. Swap the red and black lead connections and give it a try.
-AK2DM
07-30-2009 03:39 PM
07-30-2009 04:38 PM
Greg:
Glad to hear that. When I read that black was connected to (+), that was a 'red' flag 🙂 that warranted further information.
-AK2DM
07-30-2009 04:58 PM
Yes, connecting the black lead of the transducer to V+ seemed wrong... but it also seems unnatural to connect the black lead of the transducer to AI. I picked the wronger way!
Thanks again