01-03-2011 01:22 PM
I have a GE Humitrac 4-20mA output relative humidity, temperature sensor that I am using with the the NI 9203 board and the cDAQ 9174. Currently I have the (+) from the power supply going to the V in (I1RH/P+) terminal of the sensor. The RH RTN (I2RH/P-) terminal connected to AI0 of the 9203, the Temp RTN (I2-TMP) terminal is connected to the AI1 of the 9203, and the com (-) from the power supply connected to the com of the 9203. Both channels are set up in MAX for 4-20mA. I get zeroes on both channels when measuring ambient. The manual for the sensor can be found here Humitrac Manual.
Any suggestions? Thanks in advance.
01-04-2011 11:43 AM
Hi there,
Just to make sure that you can read values other than zero, I would try to connect a known voltage value (like a battery) between your differential terminals. Also make sure that your differential terminals are not touching. You can use a Test Panel in the Measurement and Automation Explorer for simplicity.
01-05-2011 07:36 AM
Thanks for the reply. I'm not sure I understand your suggestion, the NI 9203 is a +-20 mA board. Could you please elaborate?
Thanks.
01-06-2011 09:44 AM
Hi Clad,
Your connection looks OK to me. Have you selected the dip switch SW1 and SW3 on your sensor to current position? I would create a 4-20 current signal using a process meter and see if NI 9234 could see this signal if I were you.
01-06-2011 09:50 AM
It was my scaling factors! I created my curves using 4-20 instead of .004-.020, lesson learned ![]()
01-06-2011 09:56 AM
That happened to me as well!
It's nice to hear you got your problem solved!