11-27-2012 12:41 PM
I am also trying to do a similar thing but in my case I have 2 relative humidity transmiters with a 4-20mA + and a 4-20mA- and they are powered externally. If I connect the 4-20mA + to AI8 do I have just to connect the 4-20mA- to COM?
Any guideline will be appreciated!
11-28-2012 01:23 PM
Hello suf13,
Yes, that is the correct way to connect the current inputs.
11-28-2012 01:49 PM
I have attached the drawing depicting how I am planning to wire my Analog Input card. I am waiting on parts for the panel, so it is not actually wired yet, but this is the method I chose to try.
11-29-2012 10:32 AM
Hello wishiwasanindian,
It looks like you are using -24V as your common ground. I would be very cautious of doing this, because the 9207 Maximum working voltage for analog inputs is between +-10.2 V of common ground. So, this will only be an acceptable common ground if you are expecting to read in voltages between about -34 V and 14 V.
11-29-2012 10:47 AM
No, my common ground is at earth ground potential. It is just poor nomenaclature on my part, I labeled 24- as the return path for the 24VDC power supply. It is not -24V, but the 24 - connection to the power supply.