Programmatically Setting Digital Channels to Input or Output
Which classes/methods in Measurement Studio NIDAQ-mx support allow me to programmatically set a digital channel for input or for output? The only methods I've come across provide lists of previously-configured i/o channels.
(4,215 Views)
Accepted by palley
If you are using a device that has bi-directional digital lines, then you don't have to specifically set a channel as input ot output. Use the DAQmxCreateDIChan or DAQmxCreateDOChan channel functions with the lines that you want to use. Automatically the line will be configured as Input or Output.
If the device doesn't support bidirectional digital lines, then you cannot set a input channel as output channel and viceversa.
"A VI inside a Class is worth hundreds in the bush"
യവന്‍ പുലിയാണു കേട്ടാ!!!
(4,196 Views)
Whoops! I was a little premature in labeling your response a fix.
I haven't found that method available to me from within Measurement Studio (8.1), at least not within the documentation for .NET(2.0).
I see that it is documented in the C-language documentation. How do I get access to it or is there another strategy from within the .NET environment?
Thanks.
(4,175 Views)
You can use the CreateChannel method in NationalInstruments.DAQmx.DIChannelCollection.
If you feel that issue is not yet solved, you can uncheck the accepted solutions tag. If you mark a thread as solved, there is a chance that others may not look at it and you problem will remain unsolved.
(4,159 Views)
