Multifunction DAQ
Python - 2 * SCB68 A on NI 63 23 - 16 channel differential
Hello to all of you,
I have a problem that I don't understand at all;
I have a NI 6323 card with two SCB-68A cards as data connections.
I want to work in differential.
When I work in CSR or NRSE mode, I can access 32 channels.
When I put my terminal in DIFFERENTIAL mode, I can only have 8 channels instead of 16.
With 32 channel
def cfg_read_task(Saturation):
                  Saturation.ai_channels.add_ai_voltage_chan('/Dev1/ai0:31',min_val=0.5,max_val=1.5,
                  terminal_config = nidaqmx.constants.TerminalConfiguration(-1))
                  Saturation.timing.cfg_samp_clk_timing(rate=sampling_freq_in, sample_mode=constants.AcquisitionType.CONTINUOUS,
                  samps_per_chan=buffer_in_size_cfg)
With 8 channel and differential terminal
                  Saturation.ai_channels.add_ai_voltage_chan('/Dev1/ai0:7',min_val=0.5,max_val=1.5,
                  terminal_config = nidaqmx.constants.TerminalConfiguration(10106))
This script is working :
With 16channel and differential terminal
This script is  not working :
                  Saturation.ai_channels.add_ai_voltage_chan('/Dev1/ai0:15',min_val=0.5,max_val=1.5,
I attach my MAX image who see my two scb68-A cart.
Does anyone have any idea what I'm missing?
thanks for reading,
(1,294 Views)
Accepted by KramGeo
You're probably missing the way differential pairs are fixed in the hardware and the way the AI channels are split across the 2 connectors.
You *can* declare channels ai0:7 as differential, but that just defines the + inputs.  The device itself will then use (and expect you to physically wire) ai8:15 as the - inputs.
Similar stuff holds true for ai16:23 (+) and ai24:31 (-) on the other connector.
So your task config should designate 'Dev1/ai0:7, Dev1/ai16:23' to give you 16 total differential channels.
-Kevin P
(1,288 Views)
Hoooo Yeah, i'm dumb sometimes;
Thanks Kevin P! As usual, you have the right answer !
Version who work :
terminal_config = nidaqmx.constants.TerminalConfiguration(10106),
units=nidaqmx.constants.VoltageUnits(10348))
Saturation.ai_channels.add_ai_voltage_chan('/Dev1/ai16:23',min_val=0.5,max_val=1.5,
(1,244 Views)
