Setting up Analog Output in PCI6025E
I have a PCI6025E board that I would like to setup such that it outputs a sawtooth data.
I used a Sawtooth function signal generator (range 0-4V), which I connected to AO Continuous Gen. I want to output this to pin DAC0Out, which I set up in MAX as a channel called test.
For testing, I also set up an analog input channel, using Differential mode (using ACH0 and ACH8). I connected the pin from DAC0Out to ACH0 and AOGND to ACH8.
When I tested the results using MAX, I couldn't get a signal, and MAX shows constant 5 V output. When I use a Probe on the waveform data, it shows the sawtooth signal.
Can anyone give me a suggestion how to fix this problem? I have tried the Labview example Continuous Sine Generation and set it
up to test, but I can't get any results out of it as well.
I'm using this setup because I needed a signal generator capable of outputting a sawtooth signal, as well as trying to measure any possible losses through cables and the DAQ board.
Thanks in advance
elton
(2,989 Views)
Hello elton,
At first glace it looks like you have everything set up correctly. To replicate your situation, I modified the �Simul AIAO Buffer(E-Series).vi� example with a 0-4 v sawtooth signal. I am including copies of this modified example both with and without the input line. They both ran fine, and the copy without the input line tested great with a virtual channel in MAX. If these files don�t address your particular situation, or if you have any other questions, feel free to post a copy of your program and I would be happy to take a look.
Have a nice day!
Robert M
Robert Mortensen
Software Engineer
(2,989 Views)
Hi Robert,
Thanks for your help. Your files are similar to mine, with the exception of the sawtooth example with input line. I could not output and sample in fast enough, probably due to the limitations of 6025E (1 DMA channel)
I have run both files, and wired as per the configuration listed above (DAC0Out to ACH0 and AOGND to ACH8, as well as the 7 other differential channels), and I can't get a response from MAX either. I will ask my colleague to demonstrate his setup that was working previously
elton
(2,989 Views)
I have tested the DAQ card with an oscilloscope. It shows that the analog out is working perfectly, with the positive connected to DAC0Out and ground to AOGND.
I have tried the NI-DAQ MX self-calibration, but I am not getting any output, even through MAX test panels (AI is configured to Differential mode).
I will do some more testing before committing this to hardware malfunction.
elton
(2,989 Views)