USB 6009 Digital Input issue
          I'm using USB 6009. I've issue in Digital Input.I didnt connect anything on any channels. But all the DI/O channels generating 5 volts. And I tested the DI/Os in Test panel also.All the digital inputs are in high position . How could I use this ? Please suggest me the solution.
(5,516 Views)
What issue? With nothing connected, you should be seeing a logic one on all pins. There is nothing being 'generated' when you have an input only setup.
(5,504 Views)
Thank you for your reply. Thing is I didnt get any changes depends on input at that particular channel. I've connected 5 V to that pin ( say port 0.0) its in high and its remains the same when i remove that voltage . No changes ( high or low ) in that channel.
I have read something about USB 6009. i.e when the device is start up it will be in high state. So I used inverted input logic. Its in off state .I got the same respone. Hope you got my point. And i'm reading the voltage i.e digital input. So there is nothing to discuss about 'generate'. But I could read 5 V at all DIO channels.
(5,496 Views)
Accepted by bhar_s
You are the one that said it was generating 5V. And I said an open should be detected as a logic one. Connect a gnd to an input.
When it starts, all of the I/O default to inputs.
(5,489 Views)
Accepted by bhar_s
By mistake I put that . That is not geneating. And i've connected ground to the digital input terminal,now it works well. So I guess I should follow sourcing based connection.Thank you for your reply.
(5,482 Views)
RTFM  migth have tell you that there are pull up resistors at the DIOs ....
Greetings from Germany
Henrik
LV since v3.1
(5,442 Views)
