I'm using the USB6008 device to measure voltages ranging from 0 to 20VDC using a differential analog input.  Is there a way to setup the device to auto-range?

0 Kudos
Message 1 of 4
(3,196 Views)

No, there is no such function unless your write one.

0 Kudos
Message 2 of 4
(3,192 Views)

Be very careful with the differential measurements when trying to go up to 20V.  Each input of the differential has to be in the range of -10V to +10V relative to GND or you will damage the device.  See page 14 of the specification.



There are only two ways to tell somebody thanks: Kudos and Marked Solutions
Unofficial Forum Rules and Guidelines
"Not that we are sufficient in ourselves to claim anything as coming from us, but our sufficiency is from God" - 2 Corinthians 3:5
0 Kudos
Message 3 of 4
(3,188 Views)

The 6008's not going to read +20V very well... its range is -10 to +10 relative to ground. 

 

Use a voltage divider or 10x scope probe and multiply by that factor in software.

 

There's no "autorange" feature on the 600x boards either.  You can set it to the highest range and figure out what scale you need to be at in software if you want that feature. 