Multifunction DAQ
Wire Length for analog input in DAQ
What is the maximum length of the wire that can be used to connect the sensor output (4-20ma) to my USB-DAQ(not sure of the model) . This is important. Will the wire resistance affect the accuracy of the measurement in any way ?
(4,594 Views)
It can be up to miles, depending on numerous factors:
-Need to know what the maximum loop resistance the transmitter can handle
-Wire gauge and expected ambient temperature (this affects loop resistance)
-Voltage supplied to the transmitter
-Input resistance of DAQ card
Can you supply some numbers for the above?
Generally, 4-20mA loops are immune to noise, but it is suggested to use shielded cable.
-AK2DM
(4,583 Views)
-Need to know what the maximum loop resistance the transmitter can handle ( N/A)
-Wire gauge and expected ambient temperature (this affects loop resistance) (High Humidity , around 30 C )
-Voltage supplied to the transmitter ( Its an Electromagnetic Flow sensor, i guess it shud be maximum around 20VDC not more)
-Input resistance of DAQ card Can you supply some numbers for the above? ( not sure of this)
Generally, 4-20mA loops are immune to noise, but it is suggested to use shielded cable. ( I just need to use atleast 6 meters around 10ft of a single strand copper wire Shielded )
Thanks in advance
"THERE IS NO SPOON "
(4,563 Views)
Accepted by adith123
adith123:
6 meters (~20 feet) will be just fine.
"Follow the white rabbit" 🙂
-AK2DM
(4,551 Views)
Thanks a lot 🙂 esp from a fellow fan 😉
"What is Real ? How do you Define real ?"
(4,530 Views)