07-29-2015 12:50 PM
I am trying to wire a 100 ohm platinum RTD, 3-wire, into a channel on a NI 9217. I wired it up with RTD+ and RTD- connected to the marked terminals and the third wire connected to COM. When I run a test panel in NIMAX and check the resistance across RTD+ and RTD- with a DMM, I get the correct value (110 Ohms at ~80F). However, NIMAX shows a resistance of only ~0.5 Ohms. What am I doing wrong?
Thanks!
07-30-2015 11:36 AM
Hi Diarmaede,
I'm sorry to hear you are not getting the expected resistance in NI MAX. Here is a link describing how to connect an RTD to a DAQ Module.
http://digital.ni.com/public.nsf/allkb/5BFB36CFCC32C662862570D5006DC0C0
07-30-2015 11:39 AM
Thanks. The manual does not show the jumper between CH+ and EX+. I will give that a try.