Hi Mike,
Yes, if more than one grounded source is connected in a NRSE connection, you will get a grounding loop. And yes, the input commons are all connected to AI-Sense, no matter what the state of the multiplexer. Here is a link to a National Instruments webpage on grounding:
Ground Loops: Measuring Grounded Signal Sources
If you absolutely must use NRSE, I would suggest plugging in your measurement device and signal source into the same wall outlet to increase the chance that they will have the same ground.
I hope this helps!
- Erik