Multifunction DAQ

cancel
Showing results for 
Search instead for 
Did you mean: 

analog output ground loops

Solved!
Go to solution

Hi, 

 

I'm using a power supply (kepco BOP 100-4 if it helps) and controlling it using a PCI-6221 board. I'm also measuring the current and voltage in the load circuit using the same board.

The power supply is a floating source, but I've earthed it, so for the AI measurements  I use the differential mode. On the power supply the input and outputs have the same ground, so I was wondering if there was any risk of a ground loop due to the AO GND ?

 

 Thanks,

 

0 Kudos
Message 1 of 13
(6,684 Views)

Hi scalpas,

 

When you're using the differential connection for measurements you should not have any ground loop issues, as long as you're not actually grounding either of those connections. I am unclear on what your system looks like. If you could create a layout and connection diagram of your system that would really help me see exactly how your system is set up.

 

Also, when you say that the power supply is a floating source, what exactly do you mean? Is it not powered by a grounded plug?

 

Chris W

0 Kudos
Message 2 of 13
(6,676 Views)

Hi Chris, 

 

Thanks for your answer. I've enclosed a diagram of the setup. 

The power supply is powered by a grounded plug, so the chassis is grounded. However, the inner circuitry is isolated from the chassis ground, so the output is a floating source. I've grounded it 'manually'. I've drawn the power supply as an op amp, because basically it acts that way : it amplifies the signal it receives from the daq board.

I know there's no risk of ground loops on the measurement/power supply output side, because there's only one ground connection. However, is the AO GND output on the board actually grounded ? Or is it just called that because it's a reference potential ? 

 

 Regards,

0 Kudos
Message 3 of 13
(6,673 Views)
Solution
Accepted by scalpas

scalpas:

 

I believe all the grounds (AI, AO, digital) are tied to earth ground within the PC. If you have an ohmmeter, with the PC off and unplugged, check for continutiy between a GND pin on the DAQ and the metal case portion of the PC (case is usually wired to AC mains earth ground).

 

-AK2DM

~~~~~~~~~~~~~~~~~~~~~~~~~~
"It’s the questions that drive us.”
~~~~~~~~~~~~~~~~~~~~~~~~~~
Message 4 of 13
(6,655 Views)

Hi scalpas,

 

AK2DM is correct, the AI, AO and digital grounds are all tied together at one point and grounded through the PC bus. There is a knowledgebase article that basically states the exact same thing.

 

 http://digital.ni.com/public.nsf/allkb/02A451C0A88A3EAE8625702F0059C98E?OpenDocument

 

Chris W

Message 5 of 13
(6,649 Views)

Ok, so I probably have a ground loop right now on my setup, through AO GND and the cable I used to ground the power supply.

Thanks for your help.

0 Kudos
Message 6 of 13
(6,642 Views)

I just checked the circuit with an ohmmeter, and yes, the whole circuit is grounded through the AOGND channel.

 

Thanks! 

0 Kudos
Message 7 of 13
(6,637 Views)

Hi,

 

I am running into a similar problem.  I am using the PCI-6221 to set/read voltage and current on a power supply.  All my analog inputs are set to differential to minimize ground loop noise, however i have no choice but to reference my analog output to AO GND.  The power supply's analog input return is refereced to it's GND.  Their recommendation is to use a floating or isolated source.  Can I effectively create an floating source by using two analog outputs, AO0 set to 0V and AO1 set to 10V?

 

 

Best regards

hv

0 Kudos
Message 8 of 13
(5,716 Views)

Hi hvo123,

 

Using the two AOs should work since neither is a ground connection. I'm curious to know why you want to connect a floating source to your power supply though. I've also included links to a few resources that may be helpful.

 

Field Wiring: http://zone.ni.com/devzone/cda/tut/p/id/3344#toc2

M series manual: http://www.ni.com/pdf/manuals/371022k.pdf (page 5-6)

 

Best,

Carisa Leal

Applications Engineer
National Instruments
0 Kudos
Message 9 of 13
(5,694 Views)

hv,

 

Using two AOs like that will NOT create a floating source.  AO0 will be zero volts from AO Gnd and AO1 will be 10 V from AO Gnd.

 

Lynn

0 Kudos
Message 10 of 13
(5,687 Views)