current range analog output 6020
I want to obtain a constant current of 50mA to drive a resistive load, of atleast 20Kilohm resistance. The source must be truly constant current. Can i use the DAQ 6020 E (BNC) device to provide this current? What is the maximum current this DAQ device can source? I do have a kepco constant current power supply which can provide up to 80mA but i would still like to use the DAQ to isolate the Kepco power supply from the resistive load to protect from noise/ spike/ overvoltages- how do i connect the kepco supply to the DAQ?
(3,230 Views)
The specs can be found here. The device is not a constant current source and the max it can output is 5ma. You can't connect the kepco to the DAQ board.
(3,218 Views)
Do you realize that the source will need to have a compliance voltage of 1000 volts to source 50ma through a 20Kohm load? (.050A * 20,000 ohms) = 1000V.
What model number is the Kepco supply?
(3,207 Views)
is there any device such as an isolation amplifier etc or anything that you recommend that can electrically isolate the Kepco 500 M constant current power supply from the experimental set up consting of the resistor? I want to protect the kepco supply from dangerous overvoltages produced by experimental device.