Multifunction DAQ
the mighty 6008, measure a photodiode
I've been reviewing the forum and support pages for different 6008 issues, but I still have a few questions.
Especially how to choose between single ended or differential measurement.
I want to acquire the DC value from an amplified photodiode. http://www.thorlabs.com/thorProduct.cfm?partNumber=PDA10A
Any hint appreciated !
Cheers, Joel
(3,153 Views)
Accepted by Joel_ch
If you've got inputs available, use differential.  Bring both wires closest to the point where you want to take the measurement.
If I'm measuring a bunch of voltages across the power supply of a PCB under test, I'll take them RSE since there's plenty of voltage there and usually ±0.1V accuracy is enough to tell if things are working right or not.
Differential gets rid of common-mode noise in the wires between the DAQ and the DUT.  Also with the 6008, gives you another bit of resolution and 8 scales (RSE is fixed at 10V regardless of what you plumb into the create-channel min/max terminals).
(3,148 Views)
Thank you for your answer.
I understand there is no point using RSE unless you need a lot of channels. I'm actually using two only, so I will change my setup from RSE to differential.
Cheers
(3,105 Views)
