07-11-2005 12:56 PM
07-12-2005 03:47 PM
Hello Ricardo,
Can you tell me whether the MTBF number you needed is for a specific module or for the cRIO controller?
Please refer below for cRIO-9004 and cRIO-9002 MTBF numbers
For cRiO-9002
Hours Temperaure Method Used
13,555 40 C, 104 F MIL HDBK 217F
95,769 70 C, 158 F Bellcore Issue Level II
561,513 25 C , 77 F Bellcore Issue Level II
1,618,487 -40 C, -40 F Bellcore Issue Level II
For cRIO-9004
500,270 70 C , 158 F Bellcore Issue 6
1,253,788 25 C , 77 F Bellcore Issue 6
4,314,583 -40 C , -40 F Bellcore Issue 6
Hope this helps.
Regards,
Arun V
National Instruments
08-08-2013 01:08 PM
Is it safe to assume that these MTBF numbers apply to all of the cRio units in particular the 9014 model?