08-07-2006 01:20 PM
Good day. I would like to seek advice about monitoring 3-phase voltage at the supply point of 230V. The main aim of the project is to monitor power quality disturbances like transients, voltage swells etc. The experiment equipment consists of 3 single phase transformers, NI SCC AI01, SC2345 Shielded carrier with BLACK BOX CA-100 enclosure, and a computer.
The transformer is used to step down the voltage and to provide isolation. To measure the phase voltage, is it correct to connect the transformers in star-star,with primary wye grounded? Also, is it possible to measure line-line voltage using BNC input? If yes, how should I connect the wires? This is because the BNC input is shielded to ground through the computer ground point. That is why I have doubts about how to measuring the line-line voltage using BNC input.
Apart from the maximum input voltage, what are the other differences between the SCXI and SCC signal conditioning module? Is the experiment setup the same for both? Since transformer is used for isolation as safety measures. From what I have heard, if I connect the DAQ board directly to the supply point of 230V through a voltage step-down probe, the circuit might trip due to grounding problem, ie. the PC and DAQ device is grounded, excessive current might flow through the supply N and G. In order to fix this problem, transformer is used to provide the isolation. Is that correct?
Thank you very much for the time and help.
08-08-2006 04:38 PM
08-11-2006 01:42 PM
To: Neil S
Thanks for replying to all my questions. Now i get a better idea about the setup. : )
However may i ask for your help on some further questions below.
1. Please correct me if my understanding is wrong. The input of the SCC-AI series has 2 number of channels, differential, which are the positive terminal and negative terminal of the AI01. Since there are 2 BNC connectors per panelette, these 2 BNCs are actually for the positive and negative terminals. Negative terminal is at the lower part of the panelette. Do i need to manually configure the negative terminal, ie put an - sign to each data collected? Or is the negative terminal already a differential input in the circuit to deduct from positive terminal? Because i am quite confuse with the connections. If i connect 2 signals to 2 BNC in the same panelette, i get 2 signals on my computer instead of 1 signal. Does that mean differential process must be manually done through data manipulation?
2. The grounding of the BNC shield at the enclosure end is for noise reduction,right? Will the data measurement be affected by noise if i do not ground the shield of the BNC connector to retain isolation? because i am trying to reduce noise and prevent ground loop at the same time, but not sure how. Will transformer solve the problem by providing the electrical isolation?
Thanks again for your help. =p
08-14-2006 05:43 PM
Regards,
Hal L.